Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

snap in foam insulation

Options
has any body had a problem with this type of insulation not having a big enough r valve at (8) or the foam insulating the tubing too. Thermo snap is the product name

Comments

  • Steamfitter66
    Steamfitter66 Member Posts: 117
    Options
    It wont meet code for slab insulation.

    If thats what your asking. energy code requires r 10. I prefer EPS or XPS with mesh and ties.
  • SWEI
    SWEI Member Posts: 7,356
    Options
    Also

    it puts the tubing at the bottom of the slab.  You want it near the middle of a 4" slab (or 1-1/2" from the top of the tubing to the top of the slab.) 
This discussion has been closed.