Oversized Boiler? Or inappropriate location for pressuretrol?
john walsh_2
Member Posts: 64
In the basement of the rectory of my parish church sits a gigantic WeilMcClain Natural gas steam boiler that, although I did not yet do the calculations, seems waaaaay over-sized for the building it heats.
Whats happening is it's short cycling like a yo-yo and I can hear the pressuretrol causing it as it's click is audible.
Since changing the boiler is not an option the parish priest wants to entertain at this time anyway, I am wondering if their is anything that can be done to tame this beast a bit?
Their is one six inch riser coming out of the boiler connected to the steam main. The pressuretrols(their are two)are connected to a manifold on the opposite side of the boiler about as far from the supply main steam tapping as they can get. Can this cause a rapid rise and fall of pressure where the pressuretrols are located giving them a "false" reading? And how much can the flame be adjusted down on this boiler without causing a hazardous situation?
Whats happening is it's short cycling like a yo-yo and I can hear the pressuretrol causing it as it's click is audible.
Since changing the boiler is not an option the parish priest wants to entertain at this time anyway, I am wondering if their is anything that can be done to tame this beast a bit?
Their is one six inch riser coming out of the boiler connected to the steam main. The pressuretrols(their are two)are connected to a manifold on the opposite side of the boiler about as far from the supply main steam tapping as they can get. Can this cause a rapid rise and fall of pressure where the pressuretrols are located giving them a "false" reading? And how much can the flame be adjusted down on this boiler without causing a hazardous situation?
0
Comments
-
Pics
As long as the pressuretrol is reading the pressure in the steam chest or header, it shouldn't matter where it is located. Could you take some pictures of the installation please?
Also, what are the high and low pressures set to right now? When the cut out is reached, how long does it take before the boiler fires back up? If so, what pressures are being registered when the pressuretrol cuts out and back in?0 -
Couple of things you could try
with absolutely no guarantee that either one will work...
First, is there a way you can put one of the pressuretrols on the steam main itself? Or even (not as good) on the riser? That way it will be reading the real pressure in the system, which may not fluctuate quite so much. That one should be the controlling one -- set to perhaps 2 psi max. The other one should be the backup set to perhaps around 5 psi or so.
Then you can also put a pressure snubber on the pigtail to the controlling pressuretrol (make sure it's steam rated). That can sometimes work wonders.
Of course, if the boiler is really seriously oversized, there isn't much of anything that will help!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
@Pics
The pressuretrol settings are 2psi cutout and .5 cutin. I will try to get some pics of the beast in the near future. It was installed in 08 and seems monstorous for the application.0 -
No time at all
once it reaches it's first cutout on pressure, it drops to it's callin set point within 30 seconds or less then runs for about 45 seconds to a minute and then goes off on the high pressure limit setting. Only to repeat the cycle again and again.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements