Resources on best testing/setting for single steam pressuretrol setting?
Chris_Williams
Member Posts: 8
Hey guys,
My sister has just had her boiler replaced. She lives in the bronx, NYC and the process has been a nightmare. The contractor she worked with was really bad, after the boiler was replaced a lot of the distribution pipes started leaking and the contractor wouldn't fix them, so she had to.
She started asking me if it was operating at too high of a pressure and sent me the attached pic. I just bought Dan's book for her for a resource, but can you recommend any resources on setting and adjust the pressure troll?
My sister has just had her boiler replaced. She lives in the bronx, NYC and the process has been a nightmare. The contractor she worked with was really bad, after the boiler was replaced a lot of the distribution pipes started leaking and the contractor wouldn't fix them, so she had to.
She started asking me if it was operating at too high of a pressure and sent me the attached pic. I just bought Dan's book for her for a resource, but can you recommend any resources on setting and adjust the pressure troll?
0
Comments
-
Don't know what you mean by resources
other than us -- and our experience. Or Dan's books...
And, based on that, that pressuretrol is set way too high. The main scale should be set at 2 (setting below that can create problems with the linkage -- although it would nice to be able to set it lower) and the diff. (differential) scale should be set at 1.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Scrolling through past posts
I know there's a tons of threads on this, I'm trying to find them right now, but if anyone has the URL off the top of their head, let me know!0 -
Thanks Jamie
Thanks Jamie, would there be a risk setting the DIFF to .5 PSI?0 -
Just Slide
Just slide the Main (grey) one to 2 and the Diff (white) one to 1. That's really all there is too it.
As Jamie Hall stated, don't lower the Main below 2 or the linkage might bind up.0 -
Pressuretrol Setting
Hi- Go with Jamie's recommendations. He's very experienced. Residential steam systems operate at a maximum of 2 PSI (Even the Empire State Building's maximum is 3 PSI)
Set the Main scale at "2" and the Differential scale at "1". That means when the thermostat starts the burner, that the pressure will build to 2 PSI before the Pressuretrol shuts the burner off. As the pressure drops, the pressuretrol will then turn on the burner when the pressure reaches 1 PSI. This cycling between 1 PSI and 2 PSI will continue until the temperature setting on the thermostat is satisfied. If you want to try a sightly longer cycle you can change the Differential to "1.5" but leave the Main at "2". That means it will cycle between 1/2 PSI and 2 PSI.
- Rod0 -
Adjusting
I didn't see anyone mention if but if it has been said I'm sorry for repeating.
To adjust I believe there should be two screws on top of the unit you turn. As you turn each one the sliders will move up and down.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Manual
This shows you exactly how to adjust
https://customer.honeywell.com/resources/techlit/TechLitDocuments/60-0000s/60-2150.pdf0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements