I have to move a steam pipe to an inside wall and the pipe is 1". Can I transition to 1" copper piping for this.
0
Comments
-
Copper transition
Is this a supply pipe up by the ceiling, or a return near the floor?
Current practice suggests that only return pipes under the waterline can be copper. Copper supplies will heat up, and expand and contract more than iron, and may distort out of being straight. They will need more support from the ceiling to keep them straight.
You are lucky, this is only 1 inch pipe!--NBC0 -
Copper
The answer is no. Never. Don't do it!0 -
No. Never. Don't do it.
I'm in the "No. Never. Don't do it." camp. Period. Contractor installed new gas boiler on a new boiler incentive plan from National Grid. Despite my instructions, they switched to one inch copper for both returns after the vents that were a foot back from the ends and down into the Hartford Loop. Two weeks later a solder joint let go. That just doesn't happen with iron. (We are not even going to talk about the bull-headed "T")0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements