Paloma Pak Circulating pressure

ArthurMerc
ArthurMerc Member Posts: 6
What is the standing and circulating pressure of a PP12 Paloma Pak ?

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,612
    No less than 14 psi

    this is to insure that the water/diaphragm gas valve will open on a call for heat. I typically set them for 16 to 18 just to be safe. That is off the top of my head I would have to look it up in my Paloma Manual to be sure.
  • ArthurMerc
    ArthurMerc Member Posts: 6
    Paloma Pak pressure

    Thanks
  • ArthurMerc
    ArthurMerc Member Posts: 6
    Paloma Pak Service

    Hello Tim, Do you know of anyone in R.I.whois able to service the Paloma Pak furnace?
  • Tim McElwain
    Tim McElwain Member Posts: 4,612
    Del Grande Plumbing installed

    a lot of them so you might try them or my guy (one of my former students and techs from my days at Providence Gas) the Gas Doctor just google Gas Doctor and you will get there info.