converting gravity system to pump forst
ph
Member Posts: 11
i am looking to convert a gravity heating system to a forested pump system with a new boiler i have 2 21/2" supply's and 2 11/2" returns i am wandering how to pipe the near boiler piping
thanks in advance
thanks in advance
0
Comments
-
here are a couple...
great articles... http://www.heatinghelp.com/article-categories/332/Gravity-Hot-Water-Heating
generally speaking you can cut your piping in half and then reduce 1 pipe size. So 1" will work. DONT over pump it! a small circulator will work fine. you are trying to mimic the gravity flow.0 -
how to repipe
if this was my system how do i re-pipe it with the new boiler and pump0 -
didn't new boiler come with circulator?
Use transitions from new small pipes to old large. Supposed to be better than simple bushings. Biggest issue is expansion tank. If it's open you may want to consider closed.0