Infloor max cement temp ..
Total
Member Posts: 13
Hello People : What is the max temperature that you should put through the infloor tubing in a cement pad ?
0
Comments
-
max
150* IF need be.0 -
what is the application
140 but its rare to come close in a properly designed system.0 -
thanks
someone told me that you should never pump water hotter than 120 deg through the cement . The 150 deg is good to know . thanks0 -
more info
28 x 28 ft garage , heated with a vitodens 100 .0 -
Nice Garage
I like the urinal nice touch!
You should not need to come close to those kind of temps unless slab is not insulated, and you want to work buck naked in there.0 -
thanks
The urinal was my wife's idea and my 2 boys love it .. The pad is fully insulated and 2 inch blue Styrofoam 1 ft around the perimeter on the garage .Last winter it cost me around 1 $ a day to keep it heated at 60 deg F . Wanted to get the proper info from the people who know . appreciated and thanks0 -
only ??
Only 1 ft of insualation??? Where are u located?? Suppose to be at least to frost line and hope u have insualtion under the concrete..0 -
I read
Slab is fully insulated with 1' of perimeter insulation.
Is this NG, or LP?
Garage door opening frequently?
And yes where are you located?0 -
located
The frost here goes down 8 or 9 ft , the pad is insulated with http://www.beaverplastics.com/Insulation/insulworks.html
I'm located Near Prince Albert , Saskatchewan , Canada .
Natural gas - The door is a r 20 insulated and is opened maybe 4 times a day ..0 -
I think
Your doing fine if cost is a concern for your climate.
Are you struggling to hit a higher set point ?
150 would be a non insulated slab with a high r floor covering scenario with a high load.0 -
set point
I think according to the attached chart - If I set to between 2 and 3 , at -20 C the boiler should give 130 F ..I love the boiler , thanks for your help ..0 -
it's the surface temperature
based against the ambient temperature that dictates the slab output. Warmer surface/ cooler ambient= more output.
Rough rule of thumb is 2 btu/ square foot output for every degree difference.
So 85F surface- 60F ambient X 2 = 30 btu/ sq ft output. That should be plenty of output for your condition.
If the tube is deep in the pour you need higher supply temperatures. Or if the spacing is wide it takes more temperature to get that average slab surface temperature.
Generally 82- 85F is max. for surface temperature, before it becomes uncomfortably warm to stand on. Even lower if you are barefootedBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
thanks
I appreciate all the knowledge that you have shared, people ...0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements