Replaced the old American Standard
Dave0176
Member Posts: 1,178
After the job on Friday, this weekend I had to help my helper replace his 80 yo American Standard oil fired steam boiler. The boiler ran quite well but it was oil, had no equalizer and was just inefficient. So I sized a Williamson (Weil McLain) GSA 125 for him. The hardest part was removing that old boiler because it was enormous. I took you guys advice and ran two 2" risers outta the boiler into a 3" drop header into a 2" equalizer. All went well, the boiler runs great, however he needs to put back a few radiators that were pulled because we sized the new boiler up based on those rads. Have to get the fully complete pics
Also a friend who has been in the heating business for 45 years wanted to take a look at my job, so he came over, and the first thing he says is, this piping is not necessary, you guys wasted money and time for nothing. (Huh)!!!!!!
Pics
<a href="http://s2.photobucket.com/user/dave76/media/null_zps2e7ed618.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zps2e7ed618.jpg" alt="" /></a>
<a href="http://s2.photobucket.com/user/dave76/media/null_zps6a5e286b.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zps6a5e286b.jpg" alt="" /></a>
<a href="http://s2.photobucket.com/user/dave76/media/null_zps10264cd6.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zps10264cd6.jpg" alt="" /></a>
<a href="http://s2.photobucket.com/user/dave76/media/null_zpsecbccd93.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zpsecbccd93.jpg" alt="" /></a>
Also a friend who has been in the heating business for 45 years wanted to take a look at my job, so he came over, and the first thing he says is, this piping is not necessary, you guys wasted money and time for nothing. (Huh)!!!!!!
Pics
<a href="http://s2.photobucket.com/user/dave76/media/null_zps2e7ed618.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zps2e7ed618.jpg" alt="" /></a>
<a href="http://s2.photobucket.com/user/dave76/media/null_zps6a5e286b.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zps6a5e286b.jpg" alt="" /></a>
<a href="http://s2.photobucket.com/user/dave76/media/null_zps10264cd6.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zps10264cd6.jpg" alt="" /></a>
<a href="http://s2.photobucket.com/user/dave76/media/null_zpsecbccd93.jpg.html"><img src="http://i2.photobucket.com/albums/y49/dave76/null_zpsecbccd93.jpg" alt="" /></a>
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
0
Comments
-
45 years
Jealousy makes people say stupid things. Then again, being bad at your job can make you say stupid things, too! The only money wasted is by that guy's customers. They should hire you instead.
Nice job.0 -
another beauty
Very Nice Job Indeed!Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
thats a beauty
That's a beauty! Your firend know nuthing about steam... but one thing, while ya looking,atit with beer in ur hand.. the return steam vents should be piped back 15" from the end as per Dan's books.0 -
Vents
That's my helper and looong time friend Bert, it's his house so we were a bit more relaxed doing this job and took our time. His wife almost had a heart attack at first sight of the basement, but it cleaned up well. Unfortunately soot went everywere when took the old boiler apart.
I do have Dans book and yes I'm aware, but that's were the originals were, so I left them instead of disturbing more 80 YO pipe.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements