Weil McLain EG40
Dave0176
Member Posts: 1,178
Hi all new here, and kinda new to steam. Have installed a few systems with an old timer but have done mostly hot water and forced air. I am a licensed contractor and lately I've got a few steam replacements come up. First one will be replacing a 70 year old American Standard oil steamer. It is rated at 390 sq ft steam and fired at 1.4 gph. I did an EDR and total radiation was 285 sq ft so Weil McLain chose the EG40. My question is on header sizing, the manual calls for 2 1/2" riser and header, is this going to be enough or should I size it up to 3". He has two supply mains running to both sides of the house. Just want make sure dry steam gets to those radiators.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
0
Comments
-
Forgot to add
BTW am converting to gas. Also is a parallel flow system.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
show us
Show us the pictures of the steam bolier replacment you did ....0 -
Install
I haven't installed it yet just getting info, but will def post pics when done.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Near-Boiler Piping
The purpose of the header is to separate the steam from any water it might be carrying. To accomplish this it needs to slow the velocity to about 15 ft/sec. To determine the right pipe size for the header, you need the total output in cu. ft. per second, which can be calculated from BTUH, divided by the cross-sectional area of the pipe (in sq. ft.) to give you velocity in ft./sec. Or you could ask Joe Starosielec (aka JStar), who has worked out the numbers for the most common pipe sizes.
In general you should not use anything smaller than the riser ports as system risers. If there are two riser ports, use them, even if the manual only requires one. The boiler risers should extend to at least 18" above the maximum water level, but more is better. The header should have at least the same cross-sectional area as the risers combined. For two 2" risers, use a 3" header. There should be at least one diameter separation between the two riser connections to the header and two diameters between the last boiler riser and first system riser. The diameter of the equalizer should be the same as the header down to the water line.
Most important: if any of the pros here tell you anything different, LISTEN TO THEM. I've basically learned everything I know from them. They are the ones with the real-world experience.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thanks Hap Hazard
The EG40 boiler has two 3" riser tappings and the manual did only suggest one riser. I always wondered if you can use both those tappings.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Near boiler piping
So now another question?? Since the boiler is tapped for 3" risers, do I run two 3" risers? Seems a little big for 125,000 btu?DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
You can't really go too big
Using both risers tends to keep the water line more level when you're running full blast, and the low velocity on a vertical rise will allow even very small droplets to coalesce and fall back. Of course you may not need as big a header as if you had 2" risers. You might be able to get away with 3" pipe for the header too, but let's see what the pros say. I'd feel better with a 4" header, but 3" will cost less.
Another thing I forgot to mention above is that each main branch should be supplied by its own riser from the header. Ideally you want a full-port ball valve on each system riser. This allows you to blow down the boiler through the mud leg, but it's also good to have if you need to fix a leak without shutting off heat to the whole house.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
EG40
Weil-McClain recommends 2-1/2" for both riser and header. Working from Joe's http://www.heatinghelp.com/forum-thread/146979/Steam-Formulas numbers, I get:
Net output 104,000 BTU/hr (disregarding the pickup factor because this piping needs to handle all the heat the boiler can produce) that calls for 2-1/2" pipe. Split that in half (two risers, 52,000 BTU/hr each) and you get 2" pipe, which still leaves a 25% safety factor for imbalanced output between the tappings. I'd probably use 2" risers and a 3" header (one size up just for good measure.) Nothing wrong with using 2-1/2" or 3" risers if you can afford them.0 -
EG-40
If you click on the link in my signature you'll see how I piped my EG-45. An EG-45 is identical to the 40 other than burner size and draft hood.
I would have liked to use two 3" risers into a 4" header but simply couldn't afford it so I went with two 2" risers into a 3" header. I found it to produce very dry steam even with oily water in the beginning.
After the install make sure you skim! That will be just as important as the piping in the end. I had to skim 6 times and ended up building a wand to wash the boiler out from the inside with hot water.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Glad you showed up
You can't beat experience.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Always
glad to be helpful when possible.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
ChrisJ
Chris that is awesome looking job right there, it's burned into my head now. One question though why did you drop so much going into the header?? Wouldn't a 2" or 3" drop been enough??
Also the my guy at the supply house wants to know how you remove the plug on the second tapping because he said Weil puts them in so tight. I have 36" and 48" pipe wrenches so it shouldn't be a problem.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
BTW
Also tomorrow I'm doing another steam job for a small apartment building with separated boilers, one went bad when the tenet fired it with no water. I'm installing a Weil PEG 30 75000 btu. Question should I run a second riser?? Looking at the chart it doesn't seem like it needs it??DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Dropped
I dropped it that much because I felt it would make connecting the mains into it easier. I had never done this before and most of it was ordered by eye and then the last few pieces I had cut and threaded at a local place. Afterwards that was one of the first things I thought, would've looked better if it was up higher but I don't think it effects anything.
My block came with no plugs installed. The plug for the second riser came in a box.
I would use two 2" risers minimum on any steam boiler no matter how small. Two risers always works better than one and its really cheap to do with 2" pipe and fittings. You can probably get away with two 2" into a 2" header on a peg-30 and it will run beautifully.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Chris
ChrisJ thanks much for help.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
removing the second tapping
i read up about the candle trick of getting wax into the threads, after doing that, the tapping came out like a peice of cake.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements