Hey everyone just came from call where another company installed a hot water boiler....the left side of home heats fine but the whole right side does not....its a copper based two pipe system....it tee's to both sides of home in the pic I posted....I bleed the and no air comes out...so I believe its a flow problem....previously the home had be vacant for one year with the system drained....could these connectors be clogged? Thanks Paul s
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
pics
More picsASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Does the feed line
to the right side get hot at all, or even warm, for any significant distance beyond the T?
There could be a blockage, of course, although it isn't a bit common to have copper pipe in a closed system block up completely. On the other hand, it wouldn't take that much resistance to flow on the right side to divert almost all of the flow to the left side -- but never all of it (which is why the first question.
On the other hand, I see no way at all to balance the two side of the system in the pictures, leading me to wonder if there might not be a valve or two hiding somewhere which got shut off...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements