Viessmann & Siggy differ on efficiency at high return temp?
Retro
Member Posts: 13
in Gas Heating
It's very unlikely I can use in-floor radiant in my home bec. crawl is too low clearance to work safely and ceiling is near code min. So I'm sizing alternative emitters, and that depends on return temp. Can live with ~87% but if I'm paying for a mod con why not see if we can still con with radiators or what have you.
Conventional wisdom seems to keep return temps as low as poss for efficiency (and other reasons). For example, Siegenthaler 3rd ed p78 showing curves for a "representative" mod con indicates barely condensing at 125F, even at low fire. And at high fire, maxing out at hardly better than 90% in any case.
But Viessmann eg 222-F manual p3 indicates 95%+ with return temp of 158F at a 30% load. (222-F modulates down to under 20% where I imagine it's even more eficient.) Even at 50% load it seems to be doing some condensing.
Viessmann stipulates 20F drop in emitters - is that a gotcha?
I don't see similar info for Loch or TT, wonder about that.
Conventional wisdom seems to keep return temps as low as poss for efficiency (and other reasons). For example, Siegenthaler 3rd ed p78 showing curves for a "representative" mod con indicates barely condensing at 125F, even at low fire. And at high fire, maxing out at hardly better than 90% in any case.
But Viessmann eg 222-F manual p3 indicates 95%+ with return temp of 158F at a 30% load. (222-F modulates down to under 20% where I imagine it's even more eficient.) Even at 50% load it seems to be doing some condensing.
Viessmann stipulates 20F drop in emitters - is that a gotcha?
I don't see similar info for Loch or TT, wonder about that.
There was an error rendering this rich post.
0
Comments
-
Drop on emitters
depends on the emitters in question. 10-15ºF is typical on in-floor, modern panel rads can be sized at 25ºF or 30ºF
Remember, the sizing is done using the average of supply and return temps, so a supply of 145ºF and a return of 115ºF would be sized as 130ºF. If you size panel rads this way, you will be condensing all season.0 -
Chart
That is one confusing chart! It is not showing efficiency at a particular fixed temp. It is estimating the overall efficiency of a system with a particular design temp,outdoor reset curve and efficiency. The 1.8 or .5 defines the shape of the curve. It is not contradicting siggy's chart. It is a different chart altogether.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Lamda Pro Combustion
I'll answer your question with a question? What controls the dew point? If I can control the dew point I can condense pretty much at all times, even above that magical 127-130 degree water temp line.
Maybe this will help you understand. Its a pretty good little article.
http://www.thermalsolutions.com/news/wp-content/uploads/2013/04/High-Turndown-Condensing-Boilers.pdfThere was an error rendering this rich post.
0 -
Deleted
There was an error rendering this rich post.
0 -
Good article
Chris that is a good article.
I think the original poster was confused about the Viessmann efficiency as it pertains to the heating curves.
I am saving the article for folks considering Navien.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Navien
Navien does not capture flue gas condensation to reclaim the loss latent heat. While it may condense it still doesn't reclaim lost btu/hr through the venting system. It also does not come ODR unless the installer purchases it separately. Navien, because it has a CAFUE vs an AFUE rating isn't held to the new Sept 2012 standard. That's the story to be told when competing against it. Your correct because he only posted one part of the Viessmann chart h left out the heating curve chart which is attached.There was an error rendering this rich post.
0 -
All boilers have a set of curves like that
Viessmann is the only one I know of who publishes them widely.0 -
trying to follow your reasoning here...
Chris and Zman I think I get what you're saying - Siggy's chart is steady state efficiency - do you think the Viessmann chart must be an estimate of seasonal efficiency? I figure, probably heat+hot water for some representative household size in a climate where design temp is -4F.
Which means, everybody, yes I definitely ought to have posted Viessmann's ODR curves. What is that diagonal scale at the lower left of those curves?There was an error rendering this rich post.
0 -
Room Setpoint
That's the setpoint the boiler is using to calculate the curve. You could graph the months of the heating season with daily daytime and nightime temps and come up with your operating percentages. Might not be 100% accurate but will give you a idea of where you'd be running most of the heating season.There was an error rendering this rich post.
0 -
Dunkirk has something to say about this...
Dunkirk's Quantum Leap (discontinued I assume) advertised as follows:
"Heated condensate (from the Recovery Unit)
is sprayed down inside the Quantum Leap’s
Evaporative Re-Cooling Tower where it saturates
and heats combustion air. This raises the boiler's
dew point so that 90-plus percent efficiency can
be obtained at return water temperatures up to
160° F. The QL is the only residential boiler in
the world capable of this feat."
http://dunkirk.dev.salientlink.net/uploads/product/literature/253529d8bd958dd516417653c714da1f.pdf
While I was looking for availability (doesn't seem to be any) I also found maybe Dunkirk's name should be added to the list of makers with the smallest available mod-con boilers
http://www.dunkirk.com/product-details.asp?id=247#9
They come in 50 and 75 kBTU models and have 5:1 turndownThere was an error rendering this rich post.
0 -
Dunkirk's Quantum Leap
Yeah well, I had this boiler. Maybe that's what ate it alive from the inside out. Actually a great idea with poor execution in my humble opinion. We've learned a lot in 10 years.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements