Thermostat Question
Junkbox
Member Posts: 7
I replaced my old thermo stat with a new Honeywell RTH2510 Programmable thermostat. My problem is the old one only had 2 wires a White and Blue.
My new one does not have a digram for a 2 wire set up. It give me
B O G Y W/Aux R Rc I am lost as what to do any help would be great
My new one does not have a digram for a 2 wire set up. It give me
B O G Y W/Aux R Rc I am lost as what to do any help would be great
0
Comments
-
See page 6
of these instructions:
https://customer.honeywell.com/resources/techlit/TechLitDocuments/69-0000s/69-2421ES.pdf
I believe that you want to connect your two wires to "R" and "W/Aux".8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Also...
You'll have to follow the installer setup section to configure the thermostat to match the type of system you have.
You may want to call their tech support line for assistance.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements