boiler firing rates

steamfitter
steamfitter Member Posts: 156
What determines the firing rate of a boiler? Is it by design of the system? Is it something that's pre-determined by the boiler manufacturer? or is it strictly determined by controls like thermostats, aquastats and outdoor reset controls?

Comments

  • Tim McElwain
    Tim McElwain Member Posts: 4,633
    First of all what is on the

    rating plate of the boiler for input, determined by the manufacturer. Then it would depend on a heat loss having been done and a measurement of radiation and also type of radiation. The equipment should be set up with a combustion tester and fired at the maximum design firing rate following manufacturers instructions for CO2, O2 etc.



    From that point different controls can control modulation (outdoor reset)