How to find a leak
Garfield
Member Posts: 49
I have a triangle tube prestige 250000 btu condensing boiler that I installed about a year ago. It has several webstone ball valves and 2 heat exchangers. The boiler pressure is lower than the pressure on the other side of both exchangers. I have a small expansion tank on the boiler loop. I have a city line there with a regulator and a valve. I keep it turned off in general. About once a month the boiler shuts off on low pressure (about 8 psi i think) then I turn on the valve and get it back up to about 15 and it's fine. I understand this is adding calcium etc to the boiler loop and would like to find the leak but I don't know how. The boiler loop is 1 1/2 inch sweat copper. Thank you
0
Comments
-
leak
Check the relief valve , some times hard to see if its leaking if its piped into another drain lineThere was an error rendering this rich post.
0 -
evaporate
It's piped to the floor and i don't notice any water there unless it's sporadic and evaporating before i notice it.0 -
T&P valve
It sounds like all the piping is in the boiler room and you have no puddles.
I agree that the t&p or maybe the relief valve on the backflow preventer are suspect.
I would watch the gauge as the boiler comes up from a cold start. If it rises, check the expansion tank. It is also possible the boiler has a leak. Does the condensate line drip when the boiler is not firing?
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Condensate
Condensate does drip until the unit gets above 120 or so. How do I check the boiler for leaks?0 -
Condensate
It is supposed to drip when firing, Especially at lower temps.
If you have a cold (off) boiler with a steady drip, that is a problem.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
dripping
Is'nt the condensate from the flue gasThere was an error rendering this rich post.
0 -
Right
In the somewhat unlikely event the boiler's heat exchanger has a leak, the water will end up in the condensate line. The normal condensate comes from the combustion.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
Caleffi backflow?
The Caleffi series 573 backflow preventer is apparently leaking. There is a small spot on the floor that's dry but the inside of the pipe is wet and there is oxidation around the end where the water apparently evaporates before hitting the floor. It has always dripped a little when i opened the fill valve.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 65 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements