Trianco Mark II M2 100 start up problems
boilerbaby
Member Posts: 1
I have a this boiler that starting having problems last year with igniter not working. I pulled the igniter out and found black soot falling out. Then it started to flameout. I cleaned the combustion chamber out with a wired brush and vacuumed.Previous owner said he never cleaned it out.
I also replaced the burner(flameholder) cause it had a few cracks in it and replaced the gas valve as a precautionary. It worked fine for 2 weeks and now it has a start up problem. It cycles through a few times then the Red Flame light on the control board starts flashing. I take power off for 10-15 seconds & with the timer off and it starts right up and works great for a few days.
I replaced the igniter, no more soot or particles falling out of the combustion chamber and set the timer back 4 minutes.
On a cold start the igniter reads 54 ohms with a current draw of 3.8 amps.
On a warm start the igniter reads 68 ohms with a 3.8 current draw. The gas valve reads approx. 25v across.
The stack switch seems to operate normal.
I sealed the gas flue with speed tape.
I have a pressure diff sw on order cause its leaking water at the housing.
Could some lend a hand in my troubleshooting?
I also replaced the burner(flameholder) cause it had a few cracks in it and replaced the gas valve as a precautionary. It worked fine for 2 weeks and now it has a start up problem. It cycles through a few times then the Red Flame light on the control board starts flashing. I take power off for 10-15 seconds & with the timer off and it starts right up and works great for a few days.
I replaced the igniter, no more soot or particles falling out of the combustion chamber and set the timer back 4 minutes.
On a cold start the igniter reads 54 ohms with a current draw of 3.8 amps.
On a warm start the igniter reads 68 ohms with a 3.8 current draw. The gas valve reads approx. 25v across.
The stack switch seems to operate normal.
I sealed the gas flue with speed tape.
I have a pressure diff sw on order cause its leaking water at the housing.
Could some lend a hand in my troubleshooting?
0
Comments
-
Trianco
Those boilers are really frustrating to work on. They have fancy controls that really don't tell you what is going on.
I had a similar experience that ended up being a bad gas valve harness.
Any chance you can talk the owner into a replacement? The exchangers usually fail about now.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements