Steam Formulas
JStar
Member Posts: 2,752
So, I'm sitting in the office on a Saturday, thinking about steam like usual. Came up with a few quick reference guides for header and vent sizing. This will be a growing list, I'm sure. Feel free to improve my numbers or add to them.
Steam Formulas and Capacities
****Header Size per Maximum BTUH DOE Output****
(Based on Velocity of 15 ft/sec. to 20 ft/sec. and 1 PSI of pressure)
2" Header = 48,384 - 64,512
2.5" Header = 68,832 - 91,776
3" Header = 106,416 - 141,888
4" Header = 183,312 - 244,416
5" Header = 287,856 - 383,808
6" Header = 416,016 - 544,688
3&4 Section Boilers = 3" Header
5&6 Section Boilers = 4" Header
****Steam Venting Practical Capacities****
GORTON 1
<span style="color:#000000">1-1/2</span>" @ 25 feet
2" @ 15 feet
2-1/2" @ 10 feet
3" @ 6 feet
GORTON 2
<span style="color:#000000">1-1/2</span><span style="color:#000000">" @ 80 feet</span>
<span style="color:#000000">2" @ 50 feet</span>
<span style="color:#000000">2-1/2</span>" @ 35 feet
3" @ 20 feet
Steam Formulas and Capacities
****Header Size per Maximum BTUH DOE Output****
(Based on Velocity of 15 ft/sec. to 20 ft/sec. and 1 PSI of pressure)
2" Header = 48,384 - 64,512
2.5" Header = 68,832 - 91,776
3" Header = 106,416 - 141,888
4" Header = 183,312 - 244,416
5" Header = 287,856 - 383,808
6" Header = 416,016 - 544,688
3&4 Section Boilers = 3" Header
5&6 Section Boilers = 4" Header
****Steam Venting Practical Capacities****
GORTON 1
<span style="color:#000000">1-1/2</span>" @ 25 feet
2" @ 15 feet
2-1/2" @ 10 feet
3" @ 6 feet
GORTON 2
<span style="color:#000000">1-1/2</span><span style="color:#000000">" @ 80 feet</span>
<span style="color:#000000">2" @ 50 feet</span>
<span style="color:#000000">2-1/2</span>" @ 35 feet
3" @ 20 feet
0
Comments
-
steam drums
Bigger boilers sometimes had drums. When I think about it now, I wonder how thermal expansion was accommodated.0 -
MarkS
I used the formulas in TLAOSH and the venting charts. I don't have it on hand right now. I'll post my notes later in the week.
The only numbers I couldn't calculate were header sizing for lower pressures than 1 psi. Your system at 1 oz could probably work with a 1" header!0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements