below slab floor drains
Couple questions on floor drains. I've seen that a siphon can develop if your pipe extends too far past the p-trap without venting. I know there are lots of such drains without vents so is this really an issue or is there a special fix.
For those floor drains in the middle of the garage or in the mechanical room, do they need cleanouts? I ask because I've seen several drains with no cleanouts. I have seen drains with the a cleanout passage (that go to the other side of p-trap) in the side of the drain bowl. Other than one of these drains or a whole-house p-trap, what options do I have for small (2") floor drains clean-outs?
For those floor drains in the middle of the garage or in the mechanical room, do they need cleanouts? I ask because I've seen several drains with no cleanouts. I have seen drains with the a cleanout passage (that go to the other side of p-trap) in the side of the drain bowl. Other than one of these drains or a whole-house p-trap, what options do I have for small (2") floor drains clean-outs?
0
Comments
-
Venting
Drains in the middle of slabs are required to be vented. The vents branch off close to the trap and go to a nearby wall. There are commercial traps with cleanouts. Why do you need one? Zurn makes quite a few. Plumbing waste and vent is pretty involved. It is not something you learn quickly."If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
in Canada..
Up here a 3" P-Trap could be as far as 12' from its drain connection and not require a vent.0 -
Here is one....
solution. All in one.
http://www.siouxchief.com/products/drainage/residential/floor-drains/weldone0 -
still needs vent
That is a 2" drain which means that there will be a vent take off required within 8' of that in some form, be it individual, wet....0 -
Trap to vent distances:
In MA, a 2" trap outlet can't be more than 6' developed from a vent and 3" is 8'.
Minimum drain size under a slab is 3" with short runs of 2" allowed. You can "Wet Vent" a floor drain trap/drain with a sink drain, tied in closely to the trap where waste water from the sink will splash over into the FD trap so you won't need a trap re-sealer.
If the trap is in a garage, it is supposed to rum through a oil and gasoline interceptor.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements