410 help needed!
Timco
Member Posts: 3,040
Helping a friend diagnose 410 system but I've only done one.
Suction temp 68*, 78* day, liquid pressure 230, suction pressure 115, and top of coil is 68* or so and bottom of coil is 45*. Lots of air flow. TXV installed but non adjustable. Small Rheem system. Have not looked up the size but maybe 1.5 ton. Small.
Suction temp 68*, 78* day, liquid pressure 230, suction pressure 115, and top of coil is 68* or so and bottom of coil is 45*. Lots of air flow. TXV installed but non adjustable. Small Rheem system. Have not looked up the size but maybe 1.5 ton. Small.
Just a guy running some pipes.
0
Comments
-
Coil
Liquid side of A coil sweats bad. Top clean.Just a guy running some pipes.0 -
410
Sounds undercharged. The liquid line is at saturation temperature. Superheat of 30 possibly too high.
What was the indoor wet bulb?0 -
Wet bulb
67* in house.
My liquid line was 300 psi. Coil sweats super bad.
82* and 35% in the house. Bottom of coil super cold. Top hot.Just a guy running some pipes.0 -
AC
Undercharged. Low side pressure should be closer to 160 with about 20F superheat. Subcooling should be per manufacturer's guidelines or 8-15.0 -
Rheem chart
1.5 ton ton 13 SEER chart with matching N coil...
At 80 out, heat would run from 270 to 324, low side 105 to 165. Without knowing the load, no way to guess where in that range it would be. Usually with the house comfy, probably closer to 290 head, 140 suction. Like JStar said, 20 superheat really common out of a Rheem TXV setup, the RANL-018 calls for 11 subcool. By comparison, the cheapo cube calls for 7 subcool so look at the chart that came with the outdoor unit.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements