oil tank distance/location to burner
sandrajune
Member Posts: 5
I live on Long Island, NY and starting construction for an addition. We are removing our existing underground oil tank and now have two choices:
#1 550 gal Fiberglass in-ground oil tank
#2 Roth above ground oil tank located in detached garage 65-70 feet from burner (and under a pond and part of the addition.)
Preference, pros and cons please???
#1 550 gal Fiberglass in-ground oil tank
#2 Roth above ground oil tank located in detached garage 65-70 feet from burner (and under a pond and part of the addition.)
Preference, pros and cons please???
0
Comments
-
check your local codes, but...
here in Mass the tank must be a minimum of 5 feet away, or floor to ceiling fireproof wall if close. I would also go with the double wall above ground tank0 -
clarification please
Thank you! And is 70 feet ( in a detached garage ) too far away from the burner? It seems like such a long stretch! There would be a great deal of oil in that pipe.0 -
clarification please
Thank you! And is 70 feet ( in a detached garage ) too far away from the burner? It seems like such a long stretch! There would be a great deal of oil in that pipe.0 -
Garage
I assume garage is above or at same level as boiler? 70' horizontal is no problem. A buried line will need to be sleeved and an OSV installed at tank. The tank will have to be protected by stanchions in a garage alsoTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
garage location
all that Bob said, but we have to jack hammer lally columns into the cement floor, and your new tank should be supported by a cement floor or pad only. We install the columns where the tank can be impacted. You will most likely be gravity feeding the unit, and 70 feet should be no problem. Remember all flare fittings, positive shut offs, and fireomatic valves at tank and burner.0 -
decision
Thought I'd wrap this up by saying that we found out many insurance companies won't give insurance to a new mortgage if there is ANY kind of in-ground tank (even fiberglass.) And the 70' stretch made every guy we had come to look at it very nervous (except for the one and Robert!)
But one guy convinced us the way to go was to do a steel above ground in a "tub" right up against the house 22' from the burner. The enclosed tub can be dug down two feet into the ground, leaving only 3' exposed above ground. We plan on putting a fence around it to hide it (where we will also have the a/c unit and the garbage cans!)
Thank you all for your input. They were all very valuable to our decision.0 -
Partially buried Tank Tub?
Never seen or heard of it. Not in the I&O manual either,that doesn't mean it's not allowed but I would look into it further.
http://www.oilstoragesolutions.com/Tub%20Instructions.htmTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
oil tank
i would not partially bury oil tank, as you would not have visual proof of leakage...if it occured...0 -
hmmm
hmmm --- the link you have is the tub.... now I'll have to call the Town to see if they will approve of partially burying the tank 2' ---- THANKS!0 -
If...
the arrangement which you are describing is a steel tub, set two feet into the ground, with the tank free standing within it, in principle you should be OK since, again in principle, you will see a leak from the tank before it can get into the ground -- which is the objective of the exercise.
However.
You can't have a drain in the tub. It has to be watertight -- otherwise, if you do have a leak, the oil will get into the ground, which is exactly what you don't want it to do (or a sewer, which is even worse). Which leads to an obvious question: how do you propose to keep rain water from getting into the tub, and what are you going to do about it when water does get in? It will, you know.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
0
-
That
would work. Thanks. Never seen one of those contraptions before -- why I haunt the Wall! (well, one reason anyway...)Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I had to go look it up
but it seemed like a decent idea.0 -
containment
These are not for underground, and if it was, you would have to pour a cement pad first. This is for above ground. I would go with a Roth tank.0 -
Underground
I would check with manufacturer of Tank Tub,I have feeling they won't approve this. If they do,get it in writing for AHJTo learn more about this professional, click here to visit their ad in Find A Contractor.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements