Honeywell VS820 A 5204 Question
CAMZ
Member Posts: 1
in Gas Heating
Have a quick question regarding a Honeywell VS820 A 5204 gas valve on a pool heater. Unscrewed the phillips head screw protecting the pilot adjustment. The pilot adjustment screw was inadvertently back out all the way. My question is...is there a spring or needle or anything under the flat head adjustment screw? Just making sure I didnt lose anything. Can't find any diagrams or exploded views of the valve anywhere. Thanks in adavance...
0
Comments
-
I don't think there is
Tim will know for sure.0 -
There are no springs
it is just a throttling crew to adjust flame height, Make sure if you are adjusting it on the VS820 that you have a millivolt meter hooked up to measure the millivolt output of the pilot generator. It should be between 540 to 750 millivolts. The higher the better. Also keep in mind all pilots on gas heating valves are on line pressure there is no regulator. On the main burner gas is regulated0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements