Help! Boiler keeps shutting off
Pete123
Member Posts: 22
I have a Burnham boiler that keeps shutting off. There is a small button at the back of the radiator near the exhaust vent that apparently trips the boiler to turn off and must be pushed to have the boiler turn back on. What causes the boiler to turn off and how can I fix? Desperate!
0
Comments
-
Manual resets
are always there for a very good reason -- to tell the operator (you, in this case) that there is something amiss which needs looking into, often rather urgently.
However, without knowing which of several possible small buttons it is that you are pressing, it is a bit difficult to tell what the problem might be -- only that it is serious enough that a safety device backing up the normal operation of the boiler is operating and telling you that something is very wrong.
Can you describe it more exactly? Or better yet, post a photograph of it?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
More clarity
It is a tiny reset button on the outside of the boiler, attached to the vent. It is wired to the front of the boiler. Does that help?0 -
Boiler
DO NOT KEEP RESETTING THAT BUTTON. SERIOUSLY!!!
Call a pro. You have a serious safety hazard that needs to be fixed.0 -
not really...
can you describe the "vent" a little more?
That it's wired to the front of the boiler isn't a surprise -- it's part of the control circuit for the burner.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Blocked chimney switch
Sounds like blocked chimney switch. Can be very serious. Call a professional in.0 -
Brain fade -- good catch guys
Not being familiar with spill switches...
You are right guys, and for the original poster -- turn off the power to that boiler and get a professional in before you even think about turning it back on.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
That little button is a safety control
which is doing its job. You have a real problem there which needs professional attention. These guys are right on- call a pro NOW!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
reset button
Without seeing the actual button, this is an educated guess: It sounds like the spill switch on the flue pipe. This trips by heat, usually because of a back draft on the chimney. Sometimes caused by a blockage. This should be inspected by a professional.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements