Dacroid

What would be the downside of having a3.5ton evap coil matched to a 2 ton ac condensor?

Comments

  • Ironman
    Ironman Member Posts: 7,539
    MisMatch

    How about: overloading the compressor, little or no latent capacity, poor oil return to name a few?



    It's kinda like hooking a loaded 16 ft. utility trailer to a Ford Pinto. If you remember those?
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.