Venting, less better?
Fizz
Member Posts: 547
Recently replaced Gorton#2 main with Trane vacuum vent at suggestion of old timer, but I removed disc to prevent vacuum. Result was no different, took about 20-25 min to satisfy thermostat, then duct taped 2 of holes in vent, and heat time reduced to 18-21 minutes. Pressure remains between 1-2 oz. How is this possible?
0
Comments
-
T-stat
Is the thermostat being heated by a radiator near the start of that main? And if so, how are the rooms at the end of the main? Warm? Freezing?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Room with t-stat
Actually the radiator heating room with t-stat is last on 2nd loop off system riser. All rads heat as before.0 -
How long
How long are the mains, what size radiators and what vents are on the radiators? What size is the boiler?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Length of mains?
Don't know length of mains, but radiator EDR is 518 sq ft, there are no vents on rads as system is Richardson, 2 pipe(see prior posts). Boiler is W-M SGO 6, which we converted to gas last year. It is rated 654 sf of steam.0 -
Oh
I can't help you on that then. I have zero knowledge on that type of system.
Sorry.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Vents
Time to fill the main, or time to fill the radiators? If the radiator time reduced, it may make sense. Richardson systems only have vents on the return, so you may have forced steam through all of the radiators first, if there are indeed vents on the main.0 -
Honest guy
Thanks for your input, and honesty. Not having a problem, actually running for shorter time, with no change in heating quality.0 -
Vapour systems
can be a little fussy about venting. They like to be vented at the ends of the dry returns, rather than the mains. The mains are usually cleared by crossover traps to the dry returns.
Your results are interesting -- but if it's an improvement, leave it be!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You're right
Richardson does vent thru dry return, but they have no crossover traps either. Interesting system, and simple.0 -
Question
I have played around withe those old Trane main vents. I have a couple that are float vents as opposed to their Quick Vent, which is a little smaller in size. The float vent was designed to be used as a vent on the return piping.
Just one question... why did you decided to remove the disc? The ones I had already had the disc removed and I, and a freind both worked hard to try to replicate a workable disc, but were not successfull. So, I installed a simple swing check instead. I like vacuum. My system likes it. Steam gets around the system faster on next cycle, etc. Less air to vent if you don't let it back in.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Disc in Trane
Dave, think you're right. I removed disc because I don't have a vacuum gauge, and my low pressure gauge went 1/3 of way past 0 on face, so rather than break it I removed disc and close-off 2 of vent holes which slows down air return to system which I think makes system heat quicker as my heat satisfaction time is 18-20 min vs 20-25 min.0 -
Don't know
I'd rather vacuum and a broke gauge my self than fight the air every time on a system designed for vacuum.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Vacuum
My intention is to replace lp gauge with vacuum gauge and see what happens.0 -
Vacuum
My intention is to replace lp gauge with vacuum gauge and see what happens.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements