Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Fosta pex for steam return?

bruce_21
bruce_21 Member Posts: 241
Will fostapex survive use as condensate return piping in a steam system?

Comments

  • heatpro02920
    heatpro02920 Member Posts: 991
    I would

    call the rep and ask, I only use black pipe on steam systems and I only use pex in the ceiling and walls, for DHW and FHW systems.
  • Ironman
    Ironman Member Posts: 7,550
    Definitely not

    It's only rated for 180*. Copper is okay below the water line on returns, but no kind of pex.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
This discussion has been closed.