runing hot water loop of steam boiler
rolwak
Member Posts: 1
how to wire strap-on aquastat in relay switch tradeline r845 with hot water circulator pump
0
Comments
-
845
I am making a few assumptions here.
In the systems I normally see here it goes.
The thermostat wires to TT on the relay.
Hot power 120 volt (line) goes to #1 and #4. This powers the relay transformer and the circulator switch.
Neutral to #2
Hot (load) to circulator to #3
The next part is a little trickier. You want to use The switch at #5 and #6 in series with your aquastat switch to close the TT's on the boiler.
Run a wire from one of the boiler TT's to #5 on the 845
Run a wire from #6 to COM on the aquastat.
Run a wire from N/O on the aquastat to the other boiler TT
Leave the existing wires on the boiler TT
I would recommend an aquastat with an adjustable differential set to 10-20 degrees. This will prevent short cycling.
Post some pics if you are unsure.
Carl
"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements