to convert cast iron to steamview in prewar condo NYC
madel
Member Posts: 4
Hi,
I'd be so grateful for some advice. We are doing a gut reno of a prewar condo in NYC. It's a steam system and we are faced with the choice of building or buying new radiator covers for all of the cast iron radiators or potentially switching to a design like steamview (<a href="http://www.steamradiators.com/">http://www.steamradiators.com</a>) to save space and hopefully some money on the radiator covers.
Does anyone have any experience doing this and should we anticipate any problems?
Is there any reason we should not go ahead and do this?
As with most buildings of this kind in NYC, we don't have an individual thermostat in the apt - the temperature is controlled centrally for all units. Does that have a bearing on whether we should make the switch?
Thanks for your advice!
I'd be so grateful for some advice. We are doing a gut reno of a prewar condo in NYC. It's a steam system and we are faced with the choice of building or buying new radiator covers for all of the cast iron radiators or potentially switching to a design like steamview (<a href="http://www.steamradiators.com/">http://www.steamradiators.com</a>) to save space and hopefully some money on the radiator covers.
Does anyone have any experience doing this and should we anticipate any problems?
Is there any reason we should not go ahead and do this?
As with most buildings of this kind in NYC, we don't have an individual thermostat in the apt - the temperature is controlled centrally for all units. Does that have a bearing on whether we should make the switch?
Thanks for your advice!
0
Comments
-
Why don't you
get the radiators sandblasted and repainted? They'll look real sharp- then you won't need covers, which can really reduce a radiator's output.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
btu output
Make sure that the btu output of new radiators is equal to old radiators. Please do not try to guess. The consequentces could be dire0 -
BTU?
Hi,
Thanks for the feedback. I am not crazy about the look of the old ones uncovered but more importantly, they take up an awful lot of space.
How does one determine the BTU output of the old radiators? The steamview ones have the specs online.
Thanks again!0 -
Look Better Uncovered IMHO
Here are a few images of radiators that are cleaned up and painted. Didn't sandblast them, just scraped and wire brushed, the painted with rustoleum metalic paint.
You need to be forwarned that the steel radiators that you are thinking about using will behave very differently than cast iron. The BTU will be less and once the steam has shut off the steel radiators will cool down VERY quickly. An advantage of cast iron is the way they continue to emit heat for an extended period of time. This will most likely result in your boiler being missmatched to your system and will cost a lot in fuel economy.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Nice job refnishing.
Nice job refnishing.
I had mine sand blasted and painted by a metal refinishing place (the place does work for museums) they did not powder coat. While they looked great when new, a few years later some are peeling.
I learned my lesson... powder coat next time.
While they do take up alot of space, I find the look of old rads elegant and timeless.0 -
Radiators are usually rated in EDR (equivalent direct radiation)
But you can convert that to BTUH if you want to. First you need to identify the radiator, as accurately as possible, measure the height, multiply the number of tubes or columns by the number of sections, and look up the ratings.
Dan has a book for sale that has ratings for every radiator ever made, except one, and pictures for identification. You can order a copy from the "shop" link, above, or post some pictures and we'll see what we can do.
I can tell you without looking that the steamview radiators are way less efficient than any cast iron radiator. If you think they take up a lot of space, wait until you see how many of the steamview radiators you'd have to install to replace them.
They do look nice though.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Dave
I love that short fat one you posted. Maybe because it resembles me, I don't know.
But what is that evil looking rectangle in the floor by it!?!?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Don't fear the Air Register!
It is only for the A/C. It works quite nicely.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Ok I'll have to go back and take a look
Ok I'll have to go back and take a look and some photos to see what brand/model they are.
As for painting them to leave them bare, my architect said we shouldn't paint them white as rust will show through after a while. Is that true? Are there any work arounds for this? If I painted them to leave them bare, I'm pretty sure I'd want them white....
thanks!0 -
Rust?
If you sand them down, prime them and paint them white why would there be any rust on the exterior of the radiator? Paint protects the iron and keeps it from rusting. No?Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
you won't be sorry
You won't be sorry with those steel units.0 -
Question
In regards to those steel radiators, they say they have a 1" tapping. Is this near large enough for a 8-10,000btu radiator on a single pipe system?
I would think 10,000btus would need 1 1/4" for sure on one pipe.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Rust?
If they want to be absolutely certain, send them out to be professionally prepped and powdercoated. They will look beautiful for decades.0 -
Rust-proof White
The best finish in any color is a powdercoat finish. It provides a very attractive, uniform finish, and it is very tough. The next best thing, if you can't afford powdercoating, is Rust-Oleum High Heat. It's available in black, white, silver, and my personal favorite, almond, which is a nice, off-white color. Except for the black, it's only available in aerosol cans, and holding down the spray button long enough to put a coat of paint on a radiator is about all my finger can stand, but with enough patience you can get a decent result. I don't recommend using housepaint on radiators. Most of them aren't intended for temperatures over 200°, and they eventually crack and peel.
While I agree that painted radiators are more attractive, a bare cast iron radiator shouldn't rust unless you pour water on it. Under normal conditions, a dark gray passivation layer will form on the surface which will protect it from further oxidation unless it's scraped away.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Answer
I can't remember where I found this, but if anybody has some more reliable figures, please correct me.
≤ 24 ft.² EDR (6400 BTUh): 1"
24 – 60 ft.² EDR: 1¼"
> 60 ft.² EDR (16000 BTUh): 1½"
So, yes. 10,000 BTUh falls right in that 1¼" range.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
a White one
Here is a white one, painted with Rustoleum spray paint.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
SIL
thats is to bad they r peeling, that only means that they were not prepaired right. i've been sandblasting and painting them (with rustoleum, i mix) and have never had a problem. i've only painted my first 1 about 13 yrs. ago but my mentor has been doing it much longer (with rattle can) and swears by it.0 -
I've gotten similar results,
but only at the expense of torturing my index finger. Is that the high heat or the regular Rust-Oleum?Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
sandblasting, rustproofing, powder coating etc
WIll our GC be up to this task or should we only trust a specialist to handle it. Seems like quite an ordeal to have them taken elsewhere to be refinished but I would do it if you think that's necessary.
Any good recommendations for NYC, particularly Manhattan?0 -
I'll take
your old radiators if you are getting rid of them. lol, Dont toss them, Id think esp in a prewar bldg, iron would look more fitting. those steel ones have no style IMHOWeil McLain EGH 95 400,000 BTU single pipe steam0 -
sore finger
yes, it made for a tired finger. Actually, I have a little trigger handle thing that snaps into the top of a spray can. That worked great until they redesigned the tops of the cans.
I used standard Rustoleum, not the high heat stuff. The photos I have show here are on a hot water system in my home. I have also used the same paint with great results at the Best Mansion Apartments, which is a steam system.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
another option
why not polish them? It would be a tedious **** of a job , but it technically could be done on site. Its iron. strip them and polish the casting. Then wipe them with a light coat of oil periodically. Would look awesome. Then al youre spending $ on are abrasives and time. Just a thought. They would look like jewelry...esp if you have ornamentation on them
I used to polish iron engine blocks sometimes depending on the application back when i was a machinistWeil McLain EGH 95 400,000 BTU single pipe steam0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements