Air lock
URISteve
Member Posts: 2
I currently have a contractor with a strange little problem that appears to be an air lock on the inlet side of the pump on a hot water system. There are 2 air eliminators on this system, both a good 6 to 7 feet away from the pump and around a few elbows. The pump is on the return side of the boiler and has isolation/check flange mounting. And there doesn't appear to be any leaks in the closed loop primary/secondary system.
This only occurs about once a week and keeps the system from running. I told the contractor I would go to the job and look at it with him this morning while it is currently locked up.
I'm at somewhat of a loss. Any Ideas?
This only occurs about once a week and keeps the system from running. I told the contractor I would go to the job and look at it with him this morning while it is currently locked up.
I'm at somewhat of a loss. Any Ideas?
0
Comments
-
No ideas, but a question...
Where is the expansion tank in relation to the inlet to the pump? It should be as close as feasible to the INLET of the pump...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
NEED SOME PICS
to see whats going on. is the pump mounted in the mfr. recomended configuraton. how do we know the pump is air bound0 -
Expansion tank
Expansion tank is just around an elbow about 6 ft in front of the pump, mounted to the bottom of the air eliminator. System has been up and running for close to 10 years without any problems till now.0 -
Air
Are there automatic air vents on top of air seperators, if so they could be drawing air into system especially if your n.p.s.p ( net possitive suction press, ) at your pump goes below 0 psig. I recommend all air vents on hydronic systems be valved off after initial fill and bleed. pictures would be goodThere was an error rendering this rich post.
0 -
OK -- next question
as RJ notes, if the net positive suction pressure at your pump inlet -- or at any of the air eliminators -- drops below 0 psig, you are surely going to have a problem. So the question is: what is the pressure at the expansion tank and the pump inlet when the pump is running?Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements