Brand New rad vent staying open.
ThermalJake
Member Posts: 127
Guys:
Do brand new radiator vents sometimes arrive in a condition that they dont close? I put an old radiator into service yesterday, and the steam did not close the first vent. It was a Dole 1A adjustable. It steamed right out the top. I adjusted it u and down, tapped on it with a pen (and then a screwdriver), and once, it did diminish the steam it was providing to my basement, but never stopped. So I put in a Maid-o-mist 6; again, brand new. This one did the same thing. Although it diminished over time, so I went to bed with it in service. I woke up with low water, so I changed it to another brand new one; this time a Durst adjustsble from HD! This one seems to hold, but I want to wait till it cools to see if it opens and closes right.
I was going to buy a Gorton 6 becuause of brand loyalty ( I have some 1s and 2 along my main and at the dry return).
Jake
Do brand new radiator vents sometimes arrive in a condition that they dont close? I put an old radiator into service yesterday, and the steam did not close the first vent. It was a Dole 1A adjustable. It steamed right out the top. I adjusted it u and down, tapped on it with a pen (and then a screwdriver), and once, it did diminish the steam it was providing to my basement, but never stopped. So I put in a Maid-o-mist 6; again, brand new. This one did the same thing. Although it diminished over time, so I went to bed with it in service. I woke up with low water, so I changed it to another brand new one; this time a Durst adjustsble from HD! This one seems to hold, but I want to wait till it cools to see if it opens and closes right.
I was going to buy a Gorton 6 becuause of brand loyalty ( I have some 1s and 2 along my main and at the dry return).
Jake
There was an error rendering this rich post.
0
Comments
-
Vents
The HD vents are not the greatest quality.
What pressure is the boiler running at?0 -
about 8 oz
8 ozThere was an error rendering this rich post.
0 -
High pressure problem?
Steam pressure over 3 psi can make radiator vents into paperweights, or Xmas tree ornaments. If 2 different vents exhibit the same symptoms, then the problem is with the system being over pressured (over 2 psi).--NBC0 -
low pressure
8 ounces, not pounds.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements