Fried Taco ZVC 406 EXP - over easy
Alan (California Radiant) Forbes
Member Posts: 4,214
We installed a Taco zone valve controller 6 years ago; has worked flawlessly until I get a call from the owner that there is a burnt electrical smell in the boiler room. The culprits are some components in the controller have melted (see photos).
But before I replace the controller, I'm thinking that maybe one of the Danfoss thermal actuators has shorted, so I ohm them out. All of them save one have numbers around 130 ohms, except this one that comes up with a decimel number .132. When something like this shorts, do the numbers get this low?
But before I replace the controller, I'm thinking that maybe one of the Danfoss thermal actuators has shorted, so I ohm them out. All of them save one have numbers around 130 ohms, except this one that comes up with a decimel number .132. When something like this shorts, do the numbers get this low?
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab
Two btu per sq ft for degree difference for a slab
0
Comments
-
Shorted
Alan,
That's virtually no resistance. I'd say it's toast.
If you want to confirm, hook the actuator directly to a transformer with a 1 amp fuse in line. Then amp it when power's applied. Should be 5va or less (va = volts x amps).
Obviously, you need a sensitive enough meter or wrap the wire 10 times around an amprobe jaw and divide the reading by 10.
Was the burnt relay on the zone that the suspect actuator is connected to?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Bob
Thanks for your reply.
The blown component is on a different zone which doesn't make sense, but I'm grabbing at straws here. I'll replace the actuator and hope for the best.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements