24 volt gas valve coils failing??
pentree68
Member Posts: 2
I'm a service tech and stumped on something. I have been on 4 service calls in the last 2 weeks and discovered all the 24 volt standing pilot gas valve coils have failed. other service techs in town also reported a small rash of failed coils on standing pilot valves. different locations, different brand furnaces, different brand gas valves. when i check transformers they give me at least 27 volt output. any ideas? install new gas valve and works fine.
0
Comments
-
Any electrical storms,
power surges etc. Any number of unusual phenomena could cause this to happen, look for something that applies to all the failures. It may have just been a one time thing, pin it down so perhaps it can be preventd from happening again.0
This discussion has been closed.