Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
24 volt gas valve coils failing??
Options
pentree68
Member Posts: 2
I'm a service tech and stumped on something. I have been on 4 service calls in the last 2 weeks and discovered all the 24 volt standing pilot gas valve coils have failed. other service techs in town also reported a small rash of failed coils on standing pilot valves. different locations, different brand furnaces, different brand gas valves. when i check transformers they give me at least 27 volt output. any ideas? install new gas valve and works fine.
0
Comments
-
Any electrical storms,
power surges etc. Any number of unusual phenomena could cause this to happen, look for something that applies to all the failures. It may have just been a one time thing, pin it down so perhaps it can be preventd from happening again.0
This discussion has been closed.
Categories
- All Categories
- 85.7K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 49 Biomass
- 418 Carbon Monoxide Awareness
- 71 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.2K Gas Heating
- 92 Geothermal
- 149 Indoor-Air Quality
- 3.2K Oil Heating
- 59 Pipe Deterioration
- 847 Plumbing
- 5.8K Radiant Heating
- 371 Solar
- 14.5K Strictly Steam
- 3.2K Thermostats and Controls
- 50 Water Quality
- 38 Industry Classes
- 47 Job Opportunities
- 15 Recall Announcements