Boiler Will Not Fire Unless............

Portgas
Portgas Member Posts: 8
I have a 35 year old Utica PEG-187S steam boiler running on a millivolt system. The gas control consists of a Honeywell



VS820 with powerpile.



The boiler will not fire up unless I momentarily short the two wires going to the TH terminals on the gas control. Once the



boiler runs, it correctly shuts off on its own when the programmed thermostat temperature setting is reached.



The pilot light works. I all checked the wiring and the low water cutoff switch.



Can anyone suggest what may be causing this problem?

Comments

  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    PP

    Sounds like the power pile generator is getting weak. shorting the tt terminals bypasses the resistance in the boiler operating controls, BUT once you short the tt terminals this opens the valve - once open it doesn't take as much power to hold it open.
  • Tim McElwain
    Tim McElwain Member Posts: 4,633
    Poertgas do the following

    Go up to the top and click on Resources, then go to Library and look for Tim McElwains Closet you will find "Procedure for Troubleshooting Powerpile Systems. I hope it helps.
  • unclejohn
    unclejohn Member Posts: 1,833
    Try just

    Cleaning the powerpile. Also check all the connections for clean and tightness if thats a word. you have to remember its a millyvolt system and that means there is very little voltage to begine with.
  • Portgas
    Portgas Member Posts: 8
    That makes sense

    I rechecked and secured all connections and that seems to have solved this mystery. I concluded that when working with no more that 750 Millivolts tight connections are mandatory. I suspect it may be time to remove the powerpile and measure its output. After all it is 35 years old.



    Thanks
  • Tim McElwain
    Tim McElwain Member Posts: 4,633
    Unclejohn, not sure what you mean by

    cleaning the Powerpile? Are you talking about cleaning the pilot orifice? Cleaning the generator does nothing to improve millivolts and in fact using an abrasive could do more harm than good.



    The only way to properly diagnose a powerpile system is to take a complete set of readings with a meter and then chart them out. Just tightening connections may get you by but I can pretty safely say you will have another no heat call soon.