HELP, F09...BOILER WONT STAY ON
VANGORDERS
Member Posts: 1
HEY....I NEED HELP MY PINNACLE PI-199 REV 2 FLAMES UP BUT WONT STAY LIT, I JUST CHANGED OUT FLAME SENSOR..AND STILL A NO GO. ITS COLD AND IF I DONT GET HEAT MY RADIANT HEAT WILL BE TOAST. HALP IF YOU CAN. THANKS ALOT
0
Comments
-
F09
Proceed with caution.
Could be bad ignition, bad ground, bad gas or air supply.0 -
Also....
The troubleshooting section of the manual says to check your flue and make-up air to see if there are any obstructions
AND
check your condensate drain. It could be clogged and backing up into the fire box.8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
F09
Was the old flame rod red in color?
Check to see if the drain line is clear. Have someone pour a glass of water into the vent pipe and see if it comes out the drain line fairly fast. My guess is the drain line is plugged.
When was the boiler cleaned last?0 -
removed
deleated0 -
oops
Happy new Year0 -
Condensate trap blocked I bet. Water backed up.
When was unit last serviced? Probably build up in heat x and condensate trap. Clearing condensate trap may be temp measure but unit needs servicing once a year to help prevent shut downs. Combustion byproducts build up in combustion chamber. Good luck and Happy New year.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements