HELP, F09...BOILER WONT STAY ON

HEY....I NEED HELP MY PINNACLE PI-199 REV 2 FLAMES UP BUT WONT STAY LIT, I JUST CHANGED OUT FLAME SENSOR..AND STILL A NO GO. ITS COLD AND IF I DONT GET HEAT MY RADIANT HEAT WILL BE TOAST. HALP IF YOU CAN. THANKS ALOT

Comments

  • JStar
    JStar Member Posts: 2,752
    F09

    Proceed with caution.



    Could be bad ignition, bad ground, bad gas or air supply.
  • Also....

    The troubleshooting section of the manual says to check your flue and make-up air to see if there are any obstructions



    AND



    check your condensate drain.  It could be clogged and backing up into the fire box.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    F09

    Was the old flame rod red in color?

    Check to see if the drain line is clear. Have someone pour a glass of water into the vent pipe and see if it comes out the drain line fairly fast. My guess is the drain line is plugged.

    When was the boiler cleaned last?
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    edited December 2012
    removed

    deleated
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    edited December 2012
    oops

    Happy new Year
  • tim smith
    tim smith Member Posts: 2,752
    Condensate trap blocked I bet. Water backed up.

    When was unit last serviced? Probably build up in heat x and  condensate trap. Clearing condensate trap may be temp measure but unit needs servicing once a year to help prevent shut downs. Combustion byproducts build up in combustion chamber.  Good luck and Happy New year.