US DOE on Balancing and Tuning Single PIpe Steam
Boiler Talk
Member Posts: 139
Steam System Balancing and Tuning for Multifamily
Residential Buildings in Chicagoland - August 2012
<a href="http://www.nrel.gov/docs/fy12osti/55483.pdf">http://www.nrel.gov/docs/fy12osti/55483.pdf</a>
This is an interesting document from our government.
Residential Buildings in Chicagoland - August 2012
<a href="http://www.nrel.gov/docs/fy12osti/55483.pdf">http://www.nrel.gov/docs/fy12osti/55483.pdf</a>
This is an interesting document from our government.
0
Comments
-
Thanks for Posting This
It's nice to see steam not automatically being bashed.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
My experience in Chicago
I just gave the report a quick reading and there are a number of things which are not in step with my observations in Chicago
1) It states only 1 in 10 boilers had incorrect near boiler piping. I have found that about 95% are piped incorrectly
2) No statement is made regarding how oversized the boilers are. The Least oversized are usually right on. The typical installation, however, is about 80% oversized based on radiation.
3) It appears they did very little work with main vent balancing. This is reflected in the huge temperature differences between the hottest and coldest units. 10F difference is unacceptable.
4) The systems are supposed to be balanced before cycle controls are added (according to the control manufacturers).....this was not the case.
5) They recommend the use of Gorton radiator vents. These vents on the largest settings will overwhelm the main vents, causing system imbalance.There was an error rendering this rich post.
0 -
2" Pipe and Fittings
Ah, yes. It seems threaded pipe and fittings only go up to 2" ;-). In our area, most installers that attempt to put in residential steam boilers simply don't use any size larger.
The larger mechanical contractors construct welded boiler-breaking crowbars and call them "headers".
At least this Pamphlet does not ascribe to the "rip-it-out-and-put-in-scorched-hot-error" mentality. It's a start.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Still
they need to read Gerry and Steve's venting e-book, apply that to their projects and log the results.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Bashing
I believe it quoted " these systems were built for longivity, not efficiency". or something to that effect. There still seems to be the idea that steam is inherently inefficient. I do agree however, that it is a start. However, I've found that just completing main vent balancing alone and retuning the boiler to the proper firing rate will save about the same amount as thier study. I am glad they concluded that the three main improvements need to be studied separately. As an FYI....probably most or all the boilers in the installations they worked with were grossly oversized gas atmospherics.....the norm here in Chicago. I found an ocassional power burner in those sized buildings, but they are rare.There was an error rendering this rich post.
0 -
greening steam
Holohan's book briefly discusses enclosures. Why can't there be enclosures with dampers or shutters to regulate output ?0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements