Is it a Heat pump or and AC only
Vallejodave
Member Posts: 4
I ran across this system in a newer building the other day and got stumped.
The equipment that I was looking at had a label that that said it was a water source heat pump.
It was in a large multi story residential building. The equipment was in a closet. There was one blower fan , one compressor, two coils (one evaporator and the other a heating coil.)
Basically the equipment used water from a boiler to heat the coil when an actuator was opened by a call for heat.
The AC used a water source and the compressor.
The refrigeration system had no reversing valve.
I was wondering if I missed something or what. I thought that a heat pump by definition did heating and cooling by the use of the refrigerant systems reversing valve.
This system looked like an AC only with another coil for heating from the boiler source.
Is this a heat Pump?
Butchered?
Could have been a heat pump at one time and someone yanked the reversing valve?
Heat pumps are common in larger office buildings and condos using loop water. Rare to have hot water backup heat. Usually electric or none. But if they neutered the heating capability, then it would need something unless a totally interior zone with no heat needs.0 -
Not butchered
Thanks for the response John. This is a newer system with no modifications. Its located in San Francisco so the need for auxiliary or backup heat is not really needed .0 -
Water source heat pumps.
They are often times used in larger office areas. Most utilize cooling towers and have a boilers for the heating season where the towers will be bypassed for winter so the hot water can be utilized for not only the HP, but for perimeter base. There is literally a dozen application variations that can use the same water medium. Your system may be a heat pump, but since you stated that you don't have a rev. valve. It may be out of sight, but if you have an additional hw coil, this may be the way they heat the space in your air handler. Are you sure there is no rv?
Mike T.0 -
Mike T.0 -
Model #?
More info from the unit?0 -
Heres the Model and Serial
Mammoth
Model D019RHN
Serial H0819348880 -
no valve
Yea no reversing valve.0 -
How big?
Didn't see any Mammoth water source heat pumps starting with D. Their V-Cube is a large unit that can do a floor or floors of a commercial building. Starting with about 10 tons I believe.
It could be cooling only with water cooled condenser & hot water coil for heat.0 -
Heat pump must have a
Reversing valve or it ain't a heat pump. Put your hand on the discharge line [ unit not running of course ] and follow it. The first place it has to go is the reversing valve it if goes anywhere else its not a heat pump.0
- 120 Geothermal
- 169 Indoor-Air Quality