Peerless ect 06 2.75

Steve_210
Steve_210 Member Posts: 647
Just Done some work at this building

Gorton number 2 Main Vents, change radiator valves, Hoffman 40 radiator vents.

Question boiler has a 2 inch header installation manual calls for a 3 inch

When I suggested changing homeowner wants to know what benefits could Be seen from doing this

Looking for some suggestions thanks in advance guys

Comments

  • More space

    I'd say there are at least two reasons for an oversized header.  One, it slows down the steam so that any water carried along from the riser can drop out in the header and two, it provides more room for the water on the bottom of the pipe to keep separated from the steam at the top of the pipe.
    8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour

    Two btu per sq ft for degree difference for a slab
  • Steve_210
    Steve_210 Member Posts: 647
    Thank you Alan

    Problem is it does not seem to be causing any problems right now

    I guess my real question is will it improve efficiency anything

    Quite a bit of work involved and I don't want to put him to Any unnecessary expense

    The Larger Header would definitely purchase dryer steam
  • Steve_210
    Steve_210 Member Posts: 647
    edited December 2012
    ,

  • Benefits from following instructions

    Maybe this is not the time to cut out the old shrunken header.

    You could ask them to listen for wet-stem rattles in the radiators this winter, and then perhaps they will agree to have it changed in the spring.

    My guess is only a 5% difference in efficiency of fuel use, but maybe 10% in comfort.--NBC
  • Steve_210
    Steve_210 Member Posts: 647
    Thanks Nicholas

    Since posting one of 6 Tenants have complained of a radiator Spitting

    Makes you wonder how many are not Complaining

    Once they have Heat, What do they care.

    We are repiping the boiler within the next week thanks again
  • Steamhead
    Steamhead Member Posts: 17,375
    Be sure

    to take plenty of before and after pictures and post them!
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Steve_210
    Steve_210 Member Posts: 647
    Will do

    Thanks again