So, a Parallell-Flow and a Counter-Flow walk into a Tee...
JStar
Member Posts: 2,752
We just did some repiping for a customer with a lot of water hammer and cold radiators. The original steam main looked like the first picture. The 2" pipe was actually bent to make that swooping belly at the middle tee, where it drained into a dry return. The second picture is how we fixed it.
0
Comments
-
So...
what did the bartender say?
Nice work, BTW...0 -
Picture?
Hi Joe,
Could you try re-posting the picture of the corrected piping? When I try to enlarge it for my old eyes, the sketch of the old piping pops up.
Thanks! Jerry0 -
Pictures
Whenever I post from my tsblet, the pictures never upload correctly. You can open the image in a new window to view it properly.0 -
Cool
Not only does it work better, but 50 years from now, you are going to really really really confuse the next installer who sees it. Imagine the fun of someone staring at that for 45 minutes trying to figure out why it was done that way.
Cheers
Richard.There was an error rendering this rich post.
0 -
reading piping
Some people can do it. I have to make a sketch and ponder. Once you understand it's obvious. The dangerous people are the impatient ones who proceed without understanding. Clients can drive one to distraction by expecting you to know the piping after a quick glance. JStar's work is excellent but it will confound the impatient.0 -
Thanks
I just think it's all really cool stuff. I bet everyone on this site gets a mention in the year 3012 edition of The Lost Art.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 423 Carbon Monoxide Awareness
- 92 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements