Adding a radiant Zone

Zeornlo
Member Posts: 1
Hello all, after much anticipation I have finally got my basement ready for heat. Originally my basement was gonna be set up with cast iron sun-rads that I converted from the old steam system to hot water. But as the project went on I had to pour a new slab so I decided to lay down tubing and go radiant. I used uponor hePex, 2 loops at about 270ft each, it's heating approx 500 sqft. I did get a radiant design done and this is what was recommended. My boiler is a gas fired non-condensing cast iron HB Smith. I have a it piped with 4 circulators one for each zone, controlled with an Argo ARM4P. The zones all feed cast iron sun rads.
I have never set up a radiant zone before so I was hoping to get some help from the forum. My intentions are this, from the current zone circulator (which pushes away from the expansion tank) into a 3 way mixing valve, into an additional circulator into my manifold. Coming out of the manifold to a T which brings me into a bypass loop and then back to my mixing valve, which would close my loop. I will be using a uponor 501s set-point control.
Would this be a suitable set-up?
Do I need another relay to operate my second circulator or can it operate off of my current Argo ARM4P which is where the zone circulator is hooked up?
If I do need another relay how is that relay wired in to my current system and what type is recommended?
I get a bit confused with all the different controls that start to come in to play when adding them into the current system.
Thanks for the help.
I have never set up a radiant zone before so I was hoping to get some help from the forum. My intentions are this, from the current zone circulator (which pushes away from the expansion tank) into a 3 way mixing valve, into an additional circulator into my manifold. Coming out of the manifold to a T which brings me into a bypass loop and then back to my mixing valve, which would close my loop. I will be using a uponor 501s set-point control.
Would this be a suitable set-up?
Do I need another relay to operate my second circulator or can it operate off of my current Argo ARM4P which is where the zone circulator is hooked up?
If I do need another relay how is that relay wired in to my current system and what type is recommended?
I get a bit confused with all the different controls that start to come in to play when adding them into the current system.
Thanks for the help.
0
Comments
-
You don't need
two circulators. One on the mixed line is enough. Look here:
http://www.mvsupply.biz/hrh_multiple_zone_schematic.htm8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hourTwo btu/ per sq ft for degree difference for a slab0 -
Adding a radiant Zone
If I looking at the piping schematic the correct way, it is different than what I have in my current set-up as I have a circulator for every zone. 3 of my zones are on cast iron rads the other zone would be my radiant. All as main circulators for the loop. Heres a few picks. Wouldn't I still need to put another circulator after the mixing valve regardless. Or can I move the circulator after the mixing valve? The Black one in the picture is for the basement radiant.0
This discussion has been closed.
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.8K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 772 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 19 Recall Announcements