zone issue

i need to replace a zone valve with a circulation pump. Does anyone know how I would go about wiring the pump to the t/stat?

thanks

Comments

  • Paul48
    Paul48 Member Posts: 4,469
    Yes

    Via a switching relay.
  • billtwocase
    billtwocase Member Posts: 2,385
    Why?

    You need a separate relay, flow check, and knowledge of piping. Why do you need to replace a zone valve with a circ?
  • icesailor
    icesailor Member Posts: 7,265
    Why:

    Ditto (To the question of Billtwocase).
  • unclejohn
    unclejohn Member Posts: 1,833
    Yes

    Get a RIB [relay in a box] break the 110v to the circ. through the normaly open contacts and wire the t'stat the 24v coil. Done