One pipe counterflow system

ddr
ddr Member Posts: 14
Recently had two steam systems, both one pipe counter-flow, that were excessively noisy--banging in radiation, piping etc.  Neither of these systems have any main line vents.  It seems to me that installing them would help alliviate the problem.  Am I right in thinking this?  Pitch on mains seems OK.  Radiator vents are new.  Radiator valves are fully open and radiators are pitched correctly.



Thanks,

Derek

Comments

  • BobC
    BobC Member Posts: 5,502
    Yes

    Main air vents should be added near the end of a counterflow main. make sure the vent has enough capacity to vent the main quickly. Also make sure the boiler water is clean.



    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Rod
    Rod Posts: 2,067
    Counterflow Systems

    Hi- Attached is a drawing that might be of help. Adding main vents should make a big difference. You might also check the radiator venting as quite often to compensate for lack of main vents, there are large capacity vents,  like Vari Valves, installed on the radiators. Large vents produce a large amount of condensate. This collides with the incoming steam and produces noise.  If there are VariValves turn them down to close to their minimum setting (they don't turn off) or use a regular radiator vent.

    - Rod
  • jumper
    jumper Member Posts: 2,385
    counterflow can work well

    counterflow can work well especially with drips like in Rod's diagram.