hartford loop height
TomM
Posts: 233
install manual says 2" below normal water line.
-
is that 2" to the top of the close nipple, or to the center of the nipple? i guess the lower the better to avoid hammer, correct?
-
Thanks!
-
is that 2" to the top of the close nipple, or to the center of the nipple? i guess the lower the better to avoid hammer, correct?
-
Thanks!
There was an error rendering this rich post.
0
Comments
-
From Top of close nipple
I just did some reading to see what the manufacturers say about it. Burnham v9 instructions simply say 2-4" from the normal water line. Weil-McLain for the 80 series say 4" from the normal water line to the top of the close nipple connection of the Hartford loop.
So, I would go with a measurement from the top, just to be safe.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Hartford
or Gifford? I've read Henry's articles on it, but am curious if others here have direct experience with using a Gifford Loop.0
This discussion has been closed.
Categories
- All Categories
- 86.4K THE MAIN WALL
- 3K A-C, Heat Pumps & Refrigeration
- 51 Biomass
- 419 Carbon Monoxide Awareness
- 91 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 922 Plumbing
- 6.1K Radiant Heating
- 375 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 16 Recall Announcements