Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Taco Switching Relay
MechTech_2
Member Posts: 84
Can I apply 24VAC across the R & W terminals on the t-stat input connections as a demand?
0
Comments
-
No if you do you
will burn out the transformer in the relay. The connections to R and W have to be dry contacts such as thermostat, aquastat, or end switch on a zone valve.0 -
Dry contacts...
Tim, I think he means to jump out the terminals. No, do not apply 24 vac, yes jump out or dry contacts like in your t-stat. Board provides it own power so do not ad any other t-former.
Peace
Mike T.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements