Mikesask
Member Posts: 4
I just had a IBC SL20-115 boiler installed into my shop on Thursday.
Last night when I went to empty the condensation pail I noticed that the boiler had stopped working. The message reads "Error ! Insufficient water pressure". I unplugged it for 30 seconds, when it rebooted it came back with the same message.
FYI the condensation pail is 20 L. Just have not run it to a drain yet but it would fill in 8 hours when it was working. I'm guessing that doesn't have any thing to do with it but thought I would let you know.
What should I do ?
The guy who installed it just left on holidays so I can't get a hold of him.
Last night when I went to empty the condensation pail I noticed that the boiler had stopped working. The message reads "Error ! Insufficient water pressure". I unplugged it for 30 seconds, when it rebooted it came back with the same message.
FYI the condensation pail is 20 L. Just have not run it to a drain yet but it would fill in 8 hours when it was working. I'm guessing that doesn't have any thing to do with it but thought I would let you know.
What should I do ?
The guy who installed it just left on holidays so I can't get a hold of him.
0
Comments
-
Insufficient water pressure
I am thinking you may have insufficient water pressure. What does the gauge read? Does the system have an automatic fill valve? The condensate produced by the boiler is not the same water that is in you system. It is a byproduct of combustion.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
The main status screen
displays the water pressure in psi. If it's below 4 psi (I think, can't remember the exact psi) the boiler will not fire.0 -
Low water error
Being boiler just installed you may have trapped air in heat exchanger
Check boiler pressure purge system if need be and restart
Good luck
JimThere was an error rendering this rich post.
0 -
Thank you
So I went and purchased a pony pump to put some water into the system. ( no water out in the shop yet ) So I opened the water valve after turning on the pump and it went up to just over 5 psi and then the error went to check "ignition module" and some of the seals started to leak a little bit of water. when I turned the valve off and then the pump the pressure went down to 0 and the original error message came back on.
What should I try/do now ?
Thanks in advance,
Mike0 -
Knowing you don't have a water feed to it helps
I hope you didn't freeze it? Installer should have warned you about low water, as air is eliminated it needs more feed water.
Try filling it up to 20 psi (hope he put an expansion tank on it) turn it off first and then restart it0 -
Knowing you don't have a water feed to it helps
I hope you didn't freeze it? Installer should have warned you about low water, as air is eliminated it needs more feed water.
Try filling it up to 20 psi (hope he put an expansion tank on it) turn it off first and then restart it0 -
how many times
Thank you for your input. I was able to put 17.7 psi into it and it is running again.
I have 4000 feet ( 16 runs of 250 each ) of heat pipe. Any idea of how many times I will need to add water do it ?
Cheers !0 -
Got a loooong garden hose?
I did a low mass system that I estimate has about 15 gallons of water in it. I put about 20 PSI of water in the system and closed the ball valve by the pressure reducing valve. The pressure went down to about 12 psi in about a week (cold) and remains there.
I think it is a safe bet to assume you have a bit more than 15 gallons of water in your system so you will have to add water a few more times. How far is your shop from an outside water spicket?0 -
distance
It's about 150 feet. and I'm in Saskatoon.0 -
Wait A Minute!
What kind of shop has 3/4 of a mile of heating pipe?
If I put a radial arm saw in there, could I also fit a jigsaw?0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements