750mv honeywell valve

HEATONHEATON Member Posts: 117
on a vs820a1047: is polarity important on the placement of leads fr th generator to the valve? Also is 600 mv enough to function? new valve, 600 fr generator,pilot looks ok on inpinge, valve wont open!! frustrated over the hill svc tech still working, John THANX

Comments

  • Paul48Paul48 Member Posts: 4,492
    GO

    to the top of the page....Resources.......The Library......Tim McElwain's Closet.
  • HEATONHEATON Member Posts: 117
    ok for 1 question

    charts are great for the performance troubleshoot but still need to know about polarity? thanx
  • Tim McElwainTim McElwain Member Posts: 4,389
    Polarity does not matter

    By the way open circuit should be 750 millivolts and no less than 540.