750mv honeywell valve
HEATON
Member Posts: 118
on a vs820a1047: is polarity important on the placement of leads fr th generator to the valve? Also is 600 mv enough to function? new valve, 600 fr generator,pilot looks ok on inpinge, valve wont open!! frustrated over the hill svc tech still working, John THANX
0
Comments
-
GO
to the top of the page....Resources.......The Library......Tim McElwain's Closet.0 -
ok for 1 question
charts are great for the performance troubleshoot but still need to know about polarity? thanx0 -
Polarity does not matter
By the way open circuit should be 750 millivolts and no less than 540.0