Circulator size needed

spacoli
spacoli Member Posts: 61
Hi to all. I have a room with around 10,000 btu heat loss with two  equal loops (235 feet) of 1/2 inch pex radiant floor in concrete.



I need a circulator size with a typical supply and return type manifold (home made tees),required ball valves and mixing valve. Any info, thought or opinions appreciated. Thanks

Comments

  • Zman
    Zman Member Posts: 7,561
    15-58

    I would say Grundfos 15-58

    Ideally you will push about 2 gpm at a delta t of 10. The nice thing with the 15-58 is you can dial in the speed to get your delta t correct.

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein
  • spacoli
    spacoli Member Posts: 61
    Thanks

    Carl, Thank you for your reply. I will give it a try.