gas conversion safeties

ed wallace
Member Posts: 1,613
in Gas Heating
On an oil boiler with a carlin gas conversion burner what safeties need to be added my thoughts are a rollout swicth and a double acting barometric damper any others needed
0
Comments
-
Not a rollout switch
a "blocked-flue" switch that mounts on the double-swing barometric.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0