gas conversion safeties

Options
ed wallace
ed wallace Member Posts: 1,613
On an oil boiler with a carlin gas conversion burner what safeties need to be added my thoughts are a rollout swicth and a double acting barometric damper any others needed

Comments

  • Steamhead
    Steamhead Member Posts: 16,842
    Options
    Not a rollout switch

    a "blocked-flue" switch that mounts on the double-swing barometric.
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting