sizing the DHW for a 54 unit apt.building using 37 gal/apt/day usage and figuring a delta T of 85F
so 54 X 37 X 85 X 8.34 = 14,163,822.2 BTU needed/day
ok now Seigenthaler in his book Modern Hydronic Heating p634 used a peak load of 11.6% of the time
so taking a round # of 15%
14,163,822 X 0.15= 198,293.5BTUH X 85% efficient boiler gives
198,293/.85= 233,286 BTUh
so a 270,000 BTU boiler with two 119 gal storage tanks as a buffer should be able to handle the DHW load.
Am I correct or can someone tell me why this reasoning is faulty???
so 54 X 37 X 85 X 8.34 = 14,163,822.2 BTU needed/day
ok now Seigenthaler in his book Modern Hydronic Heating p634 used a peak load of 11.6% of the time
so taking a round # of 15%
14,163,822 X 0.15= 198,293.5BTUH X 85% efficient boiler gives
198,293/.85= 233,286 BTUh
so a 270,000 BTU boiler with two 119 gal storage tanks as a buffer should be able to handle the DHW load.
Am I correct or can someone tell me why this reasoning is faulty???
0
Comments
-
Gallons per day
You are doing the math correctly.
I would be careful of the gallons per day number. What is the flow rate at the shower?Is it new construction?
It is interesting that Siggy does not discuss the relationship between production and storage. This link has some useful info.
http://www.laars.com/LinkClick.aspx?fileticket=pxQlTDrnWgo%3d&tabid=1611&mid=4041
I suspect your numbers are a bit low.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
37g/apt/day?
Not sure how you figured this usage number.... so I'm not saying it's wrong.
However, I've been led to believe that 20g DHW per person is the typical usage. The problem is, I can't remember where I saw it documented or if it was something in conversation.
That being said, if you went with 20g/day/occupant... you'd have to estimate the average occupant load per apartment.0 -
Correct Math
Your math is correct... the 270k BTU boiler can handle the 2 119 gallons dhw tanks. Especially if you plumb the two tanks in parallel on the domestic side, so the domestic water is drawn evenly through the two tanks.
The question I cannot answer is if the load of 37g/day/apt is good, but if thats a standard across the county, it sounds like you're good to go.0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements