WM SGO-3 short cycling even when t-stat is satisfied!
blackpenny
Member Posts: 15
I just (today) installed a WM sgo-3 in my home and it is short cycling even after the t-stat is satisfied. I'm very confused in my very warm home. I have 1200sq and will be adding a hot water loop tomorrow. I skimmed the boiler several times and nothing seems to help. I have 2 main air vents that are fairly new. Thanks in advance.
0
Comments
-
What kind of LWCO did that come with?
And how often is it cycling?Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Thermostat wiring problem
Are you saying that even after the thermostat has been satisfied and cut off the circuit to the boiler, it continues to run in a short-cycling fashion?
The wiring must be the problem. Doublecheck it against the diagram from the boiler mfg, and thermostat co.--NBC0 -
The thermostat
should shut the boiler off when you get to the preset temperature. Tell your installer that they might have a wire crossed.0 -
Checked the wiring
The boiler came with a CyleGard LWC. As far as the wiring is concerned it is a simple TR and TW connection to the Beckett burner.0 -
EDR
What was the total EDR of all the radiators, and how many sq/ft of steam is the boiler rated for?0 -
Installer sucks
I am the installer! lol0 -
I'm laughing too
I thought you were the victum of the installer. What kind of thermostat do you have?0 -
Honeywell t-stat
I have a digital/programmable Honeywell 5-2 t-stat. I'm not the best when it comes to steam, I do all supermarket service work now and haven't touched a steam boiler other than my own in over 7 years.0 -
Boiler
Disconnect the thermostat. See if it still happens.0 -
Read the CycleGard Manual
I think you'll find your answer there.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Do you
have an aquastat?0 -
beckett A/C ready kit???
t-stat disconnected and still happening.
ok, go easy on me ....but, ....the burner came with a jumper on R to W. Do i leave this in?
Also read in the beckett manual that I may need a A/C ready kit if boiler is cycling. ???0 -
aquastat
no auquastat ....yet. I will install one when i add my hot water loop tomorrow.0 -
I think you've bypassed the thermostat.
The LWCO turns off the burner for 90 seconds every 10 minutes. Apparently this is the only thing that's controlling your gas valve. Go over the wiring diagram inside the CycleGard cover or the one in the manual. If you connected the optional connection from the "burner" terminal to the gas valve, disconnect it and see if the thermostat works. If it does, make sure you are connecting the right gas valve terminal to the "burner" terminal.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
The
jumper(resistor) between T-T on primary control was cut?0 -
hmmmm
The beckett burner came with a jumper from W to R, so I removed my t-stat wires going to W R and it's still running. So the question is, where do I connect my t-stat wires? Looked at the wiring diagram on the cyclegard and I dont see where my t-stat connection would be. It's late and I'm confused after a very long solo install on a 600lb boiler.0 -
-
T-stat wires
Where do I connect my t-stat wires if not on the burner???0 -
Tstat
The tstat goes to R and W without a jumper.0 -
I don't get it.
I have t-stat to r and w without jumper and nothing! I'm so tired and frustrated. I just don't get it.0 -
LWC
Do I need to wire anything to my LWC??? Are the t-stat wires direct from my t-stat to the R and W on the 7505 on the burner?0 -
Post a photo of your burner control
Please post a photo of your burner control's wiring, and let us know what model it is.There was an error rendering this rich post.
0 -
Beckett Genisys 7505
I have my t-stat wired directly to the R and W on the 7505.0 -
-
yes
the one on the left without the display.0 -
Anyone???
I ran all new t-stat wire from first floor to burner. Still not running. Boiler only runs with jumper from TW to TR on burner and will not shut off when t-stat is satisfied.0 -
SOLVED!
Bad t-stat wire. I ran new from first floor to my jumper split by my water feed valve but forgot to run from there to the boiler. Wow! I can be real dumb sometimes!!!0 -
Okay, and do the LWCO and pressuretrol still turn it off?
Make sure that the CycleGard turns off the burner on low water (amber light) and for the intermittent level test (green light). Also tip the rocker on the pressuretrol and make sure it cuts the burner.
And did you say you had a water feeder too? No wonder you were confused. I installed a CycleGard and a water feeder last year, on a 30 year old Peerless. Of course the manual for the burner control didn't say where to connect a water feeder, and the Hydrolevel manuals weren't too clear on how to install their controls on a 30 year old Honeywell burner control, so I put all the manuals together and sketched out the connections and hooked everything up and... nothing. So I stepped back and took another shot and finally figure out that I needed to run another pair of wires from the transformer, which someone thoughtfully installed under my breaker box instead of anywhere near the boiler. Good times!
Oh, and by the way, I used to be an electronics technician, so don't feel bad about not getting your wiring right on the first try.Just another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
done
everything seems to be functioning as they should. i'll be starting on my hot water loop in a bit. thanks all.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements