Here We Go Again

Hoog23
Hoog23 Member Posts: 19
Last year we converted from oil to gas and installed a Smith G8 Steam boiler with an EZ-Gas.  So long story short we sold that house and bought another one.



The 'new' house has the original mid-80's gas hot water boiler and a 2nd boiler was installed mid-90's when the basement was finished.  Also has a 10 yr old smith gas water heater.



5 zones.  I would trash the 2nd boiler.



House has standard baseboard copper finned radiators. 



Chimney has a steal liner (it's not masonry).



What are my options?



Would it make sense to do another G8 (hot water) with and EZ-Gas burner?



Burnham ES2?  (Does the liner need to be insulated?).



I'm researching the mod-con idea.  I do have a outside wall in the boiler room next to the chimney that is not near any windows that should be easy to penetrate.

Comments

  • I"d keep one old one

    as a back up and/or for heavy loads and baseload with a little modcon.

    There was an error rendering this rich post.

  • icesailor
    icesailor Member Posts: 7,265
    Old boilers:

    I'd trash them both, go with a Mod/Con, direct vented out the side, and pipe allowances for a future Indirect.

    I wouldn't want that Gar-Baage' in MY cellar.